#1
We have an issue with a gate we're trying to diagnose and I'm a little stumped. Set up is as follows

Nice MC824H control panel
2x LFAB4024 in ground motors
pair of F210B photocells (addressed as FOTO)
Safety edge on one leaf of the gate
Finger keepers at each hinge
Open command is all via Paxton Net2 ACU

System is only about 6 months old so I suspect not a failed motor, especially as it seems to function correctly 90% of the time and is only really an issue when a second car nips through before the gates have begun to shut properly (which is a separate issue!)

The issue we're having is that the gate functions correctly, except when the photocell is interupted or an open command is recieved at the very beginning of the closing cycle, when one leaf has just started to move but the other hasn't, the control panel will then go into a 'stop' state and the bluebus LED will flash 10 times indicating a motor obstruction. There doesn't appear to be any physical obstruction and the only thing that I can see that might put slightly more pressure on is the finger keepers (which I don't really want to remove as I think there is a risk of someone sticking their fingers in a narrowing gap.) Power cycling will reset the unit and it will return to normal function. Interupting photocells or sending an open command when it's further along the close cycle will re open the gates as normal and the will return to the close cycle after their 'open time' as normal.

I've adjusted the closing stops slightly and re-learnt the motors as I wondered if the point at which the gates were stopping was very slightly over extended and I'm going to increase the closing force by a point or too but I'm reluctant to increase it too much.

Any bright ideas?
Reply
#2
(27-05-2025, 09:23 AM)DaveHG Wrote: We have an issue with a gate we're trying to diagnose and I'm a little stumped. Set up is as follows

Nice MC824H control panel
2x LFAB4024 in ground motors
pair of F210B photocells (addressed as FOTO)
Safety edge on one leaf of the gate
Finger keepers at each hinge
Open command is all via Paxton Net2 ACU

System is only about 6 months old so I suspect not a failed motor, especially as it seems to function correctly 90% of the time and is only really an issue when a second car nips through before the gates have begun to shut properly (which is a separate issue!)

The issue we're having is that the gate functions correctly, except when the photocell is interupted or an open command is recieved at the very beginning of the closing cycle, when one leaf has just started to move but the other hasn't, the control panel will then go into a 'stop' state and the bluebus LED will flash 10 times indicating a motor obstruction. There doesn't appear to be any physical obstruction and the only thing that I can see that might put slightly more pressure on is the finger keepers (which I don't really want to remove as I think there is a risk of someone sticking their fingers in a narrowing gap.) Power cycling will reset the unit and it will return to normal function. Interupting photocells or sending an open command when it's further along the close cycle will re open the gates as normal and the will return to the close cycle after their 'open time' as normal.

I've adjusted the closing stops slightly and re-learnt the motors as I wondered if the point at which the gates were stopping was very slightly over extended and I'm going to increase the closing force by a point or too but I'm reluctant to increase it too much.

Any bright ideas?

Hi, 

This is a very strange issue, this could be caused by an encoder issue possibly where they are interrupted so early into the manoeuvre that it confuses the motor, it could be worth contacting Nice directly regarding this due to the issue being so peculiar. 

For your second issue when a second car goes through the gates at the last second it sounds like you need to put the board into condominium mode so that it does not react to a second trigger directly after a first.
Reply
#3
(15-08-2025, 02:11 PM)Jakedugmore Wrote:
(27-05-2025, 09:23 AM)DaveHG Wrote: We have an issue with a gate we're trying to diagnose and I'm a little stumped. Set up is as follows

Nice MC824H control panel
2x LFAB4024 in ground motors
pair of F210B photocells (addressed as FOTO)
Safety edge on one leaf of the gate
Finger keepers at each hinge
Open command is all via Paxton Net2 ACU

System is only about 6 months old so I suspect not a failed motor, especially as it seems to function correctly 90% of the time and is only really an issue when a second car nips through before the gates have begun to shut properly (which is a separate issue!)

The issue we're having is that the gate functions correctly, except when the photocell is interupted or an open command is recieved at the very beginning of the closing cycle, when one leaf has just started to move but the other hasn't, the control panel will then go into a 'stop' state and the bluebus LED will flash 10 times indicating a motor obstruction. There doesn't appear to be any physical obstruction and the only thing that I can see that might put slightly more pressure on is the finger keepers (which I don't really want to remove as I think there is a risk of someone sticking their fingers in a narrowing gap.) Power cycling will reset the unit and it will return to normal function. Interupting photocells or sending an open command when it's further along the close cycle will re open the gates as normal and the will return to the close cycle after their 'open time' as normal.

I've adjusted the closing stops slightly and re-learnt the motors as I wondered if the point at which the gates were stopping was very slightly over extended and I'm going to increase the closing force by a point or too but I'm reluctant to increase it too much.

Any bright ideas?

Hi, 

This is a very strange issue, this could be caused by an encoder issue possibly where they are interrupted so early into the manoeuvre that it confuses the motor, it could be worth contacting Nice directly regarding this due to the issue being so peculiar. 

For your second issue when a second car goes through the gates at the last second it sounds like you need to put the board into condominium mode so that it does not react to a second trigger directly after a first.

Hi Jake,

Thanks for the response, we managed to trace the fault in the end but you are on the mark with it being an encoder issue, we discovered a cable joint that had suffered a bit of moisture ingress and one of the encoder pair had corroded away.

Second issue appears to have been solved by adjusting the opening stops slightly to reduce travel.

Posting mearly as hopefully it will help someone else if they encounter the same issue!
Reply
#4
(19-08-2025, 03:37 PM)DaveHG Wrote:
(15-08-2025, 02:11 PM)Jakedugmore Wrote:
(27-05-2025, 09:23 AM)DaveHG Wrote: We have an issue with a gate we're trying to diagnose and I'm a little stumped. Set up is as follows

Nice MC824H control panel
2x LFAB4024 in ground motors
pair of F210B photocells (addressed as FOTO)
Safety edge on one leaf of the gate
Finger keepers at each hinge
Open command is all via Paxton Net2 ACU

System is only about 6 months old so I suspect not a failed motor, especially as it seems to function correctly 90% of the time and is only really an issue when a second car nips through before the gates have begun to shut properly (which is a separate issue!)

The issue we're having is that the gate functions correctly, except when the photocell is interupted or an open command is recieved at the very beginning of the closing cycle, when one leaf has just started to move but the other hasn't, the control panel will then go into a 'stop' state and the bluebus LED will flash 10 times indicating a motor obstruction. There doesn't appear to be any physical obstruction and the only thing that I can see that might put slightly more pressure on is the finger keepers (which I don't really want to remove as I think there is a risk of someone sticking their fingers in a narrowing gap.) Power cycling will reset the unit and it will return to normal function. Interupting photocells or sending an open command when it's further along the close cycle will re open the gates as normal and the will return to the close cycle after their 'open time' as normal.

I've adjusted the closing stops slightly and re-learnt the motors as I wondered if the point at which the gates were stopping was very slightly over extended and I'm going to increase the closing force by a point or too but I'm reluctant to increase it too much.

Any bright ideas?

Hi, 

This is a very strange issue, this could be caused by an encoder issue possibly where they are interrupted so early into the manoeuvre that it confuses the motor, it could be worth contacting Nice directly regarding this due to the issue being so peculiar. 

For your second issue when a second car goes through the gates at the last second it sounds like you need to put the board into condominium mode so that it does not react to a second trigger directly after a first.

Hi Jake,

Thanks for the response, we managed to trace the fault in the end but you are on the mark with it being an encoder issue, we discovered a cable joint that had suffered a bit of moisture ingress and one of the encoder pair had corroded away.

Second issue appears to have been solved by adjusting the opening stops slightly to reduce travel.

Posting mearly as hopefully it will help someone else if they encounter the same issue!
Glad to hear this has been resolved, 

If you have any further queries do not hesitate to contact our technical team at technical@easygates.co.uk
Reply


Possibly Related Threads…
Thread Author Replies Views Last Post
  Nice Robus closing after photo Nexur 1 7,662 26-08-2025, 01:47 PM
Last Post: Jakedugmore
  Nice gates don’t close after the ambient temp is high Howard 2 8,357 15-08-2025, 02:01 PM
Last Post: Jakedugmore
  Nice Control unit passcode removal Andruelectricgates 1 4,038 17-06-2025, 11:25 AM
Last Post: HarrisonN
  NICE gates open slightly then stuck Overthefence 2 4,712 21-05-2025, 10:54 AM
Last Post: Jakedugmore
  Nice Robus 250 HS Fuse Problem GLM 1 4,821 09-05-2025, 01:07 PM
Last Post: Aiden Mitton
  Fuse keeps failing kite420 1 3,118 13-03-2025, 09:56 AM
Last Post: benbrooks
  Looking for help with oldschool NICE gate motor gatekeeper 0 5,440 16-02-2025, 05:16 PM
Last Post: gatekeeper
  Diagnosing Nice SFAB2024 (ex XME2024) Motors devlinjayse 0 3,237 08-02-2025, 07:22 PM
Last Post: devlinjayse
  Nice RB600 - Automatic close fail and opening issues P100D 6 9,913 10-12-2024, 11:29 AM
Last Post: P100D
  Nice MC824H Set Up issue dmrgate 2 8,365 10-12-2024, 10:31 AM