  • 33 Vote(s) - 2.82 Average
Nice LFAB occasionally failing open
(15-08-2025, 02:11 PM)Jakedugmore Wrote:
(27-05-2025, 09:23 AM)DaveHG Wrote: We have an issue with a gate we're trying to diagnose and I'm a little stumped. Set up is as follows
Nice MC824H control panel
2x LFAB4024 in ground motors
pair of F210B photocells (addressed as FOTO)
Safety edge on one leaf of the gate
Finger keepers at each hinge
Open command is all via Paxton Net2 ACU
System is only about 6 months old so I suspect not a failed motor, especially as it seems to function correctly 90% of the time and is only really an issue when a second car nips through before the gates have begun to shut properly (which is a separate issue!)
The issue we're having is that the gate functions correctly, except when the photocell is interupted or an open command is recieved at the very beginning of the closing cycle, when one leaf has just started to move but the other hasn't, the control panel will then go into a 'stop' state and the bluebus LED will flash 10 times indicating a motor obstruction. There doesn't appear to be any physical obstruction and the only thing that I can see that might put slightly more pressure on is the finger keepers (which I don't really want to remove as I think there is a risk of someone sticking their fingers in a narrowing gap.) Power cycling will reset the unit and it will return to normal function. Interupting photocells or sending an open command when it's further along the close cycle will re open the gates as normal and the will return to the close cycle after their 'open time' as normal.
I've adjusted the closing stops slightly and re-learnt the motors as I wondered if the point at which the gates were stopping was very slightly over extended and I'm going to increase the closing force by a point or too but I'm reluctant to increase it too much.
Any bright ideas?
This is a very strange issue, this could be caused by an encoder issue possibly where they are interrupted so early into the manoeuvre that it confuses the motor, it could be worth contacting Nice directly regarding this due to the issue being so peculiar.
For your second issue when a second car goes through the gates at the last second it sounds like you need to put the board into condominium mode so that it does not react to a second trigger directly after a first.
Hi Jake,
Thanks for the response, we managed to trace the fault in the end but you are on the mark with it being an encoder issue, we discovered a cable joint that had suffered a bit of moisture ingress and one of the encoder pair had corroded away.
Second issue appears to have been solved by adjusting the opening stops slightly to reduce travel.
Posting mearly as hopefully it will help someone else if they encounter the same issue!
Nice LFAB occasionally failing open - by DaveHG - 27-05-2025, 09:23 AM
RE: Nice LFAB occasionally failing open - by DaveHG - 19-08-2025, 03:37 PM
  Nice gates don’t close after the ambient temp is high Howard 2 8,361 15-08-2025, 02:01 PM
Last Post: HarrisonN
  Nice Robus 250 HS Fuse Problem GLM 1 4,827 09-05-2025, 01:07 PM
  Fuse keeps failing kite420 1 3,121 13-03-2025, 09:56 AM
Last Post: devlinjayse
  Nice RB600 - Automatic close fail and opening issues P100D 6 9,918 10-12-2024, 11:29 AM
  Nice MC824H Set Up issue dmrgate 2 8,368 10-12-2024, 10:31 AM
Last Post: dmrgate