Faac gate opens when photo cell beam is broken
#1
Hi all
Any idea how to rewire faac photo cell so it doesn't open gate. 
I want it to activate when the gate is closing for safety reasons but not actually open the gate.
Inherited the system and current setup can't be right. 
Please see pic of Tx Photo cell. 
I have a 455D control board. Thanks very much.


Attached Files Image(s)
   
Reply
#2
Hi Stephen,

Photocells are generally used to stop and reopen gates when the are obstructed while the gates are closing. This is generally to avoid damaging vehicles which could be attempting to drive through as the gates start to close. It is not usually recommended to wire the photocells into the emergency stop command but I can explain how this is done below.

Going from the colours of the wires from the image you provided, you should have a green and white wire going terminal 12 and terminal 19, these will need to be removed and a wire bridge will need to be put between terminals 12 and 19. You will then need to remove the wire bridge from terminal 11 and terminal 14 and replace this with the green wire going to terminal 11 and the white going to terminal 14. If you already have wires going into terminals 11 and 14 you will need wire the 4 wires in series to allow the photocells and other STOP device to function.
Gate Automation and Access Control from EasyGates Retail Store

EasyGates Trade Store for Trade only

Smart Home Tech from The Smart and Secure Centre

Smart Home News from Smart Home Matters
Reply
#3
(17-03-2021, 11:36 AM)RyanB Wrote: Hi Stephen,

Photocells are generally used to stop and reopen gates when the are obstructed while the gates are closing. This is generally to avoid damaging vehicles which could be attempting to drive through as the gates start to close. It is not usually recommended to wire the photocells into the emergency stop command but I can explain how this is done below.

Going from the colours of the wires from the image you provided, you should have a green and white wire going terminal 12 and terminal 19, these will need to be removed and a wire bridge will need to be put between terminals 12 and 19. You will then need to remove the wire bridge from terminal 11 and terminal 14 and replace this with the green wire going to terminal 11 and the white going to terminal 14. If you already have wires going into terminals 11 and 14 you will need wire the 4 wires in series to allow the photocells and other STOP device to function.

Hi Ryan
Thanks very much for getting back to me with such a compréhensive answer. I probably didn't explain correctly but as you have pointed out....
Photocells are generally used to stop and reopen gates when the are obstructed while the gates are closing. This is generally to avoid damaging vehicles which could be attempting to drive through as the gates start to close. 
That's precisely how I want to use them. Currently the cells actually OPEN the gate when the beam is broken. They also reopen as they are closing to prevent damage which is good news BUT they also open the gates which makes a nonsense of security. I was looking to wire them so they do not actuate the gates.
Reply
#4
My apologies Stephen. It looks like the photocells were used as a device to open the gates when approached. This would also open the gates while they were closing. Revising what I have advised previously you will have a green and white wire going into 9 and 14. The wire going into 9 would need to be moved to 12 and 14.

Wiring diagram for 1 x Closing Photocells:
   


If you already have closing photocells wired into these terminals you will need to wire these as shown in the image below.

Wiring diagram for 2x Closing Photocells:
   
Gate Automation and Access Control from EasyGates Retail Store

EasyGates Trade Store for Trade only

Smart Home Tech from The Smart and Secure Centre

Smart Home News from Smart Home Matters
Reply
#5
(29-03-2021, 09:50 AM)RyanB Wrote: My apologies Stephen. It looks like the photocells were used as a device to open the gates when approached. This would also open the gates while they were closing. Revising what I have advised previously you will have a green and white wire going into 9 and 14. The wire going into 9 would need to be moved to 12 and 14.

Wiring diagram for 1 x Closing Photocells:



If you already have closing photocells wired into these terminals you will need to wire these as shown in the image below.

Wiring diagram for 2x Closing Photocells:
Reply
#6
Ryan. That's brilliant thanks very much for your help. All the best.
Reply


Possibly Related Threads…
Thread Author Replies Views Last Post
  FAAC Configure 443Hz remote to open partially, pause and close Ezylryb 3 6,610 11-11-2025, 03:33 PM
Last Post: Prem
  Faac 740D, Open further then limit, not closing emiel 1 6,604 26-08-2025, 02:23 PM
Last Post: Jakedugmore
  FAAC Eq45s , only Leaf A closing with remote Cummil2 1 4,294 13-03-2025, 10:06 AM
Last Post: benbrooks
  FAAC Eq45s , only Leaf A closing with remote Cummil2 1 4,342 13-03-2025, 10:05 AM
Last Post: benbrooks
  FACC sliding gate not responding. Kipod 2 4,857 09-12-2024, 09:24 AM
Last Post: nicenotnice
  FAAC S800 Single swing Gate not responding robhight 0 3,943 18-11-2024, 11:48 AM
Last Post: robhight
  FAAC problem dennisoates 0 3,634 30-06-2024, 04:40 PM
Last Post: dennisoates
  Intermittent ‘Stop’ command - FAAC 741 Sliding Gate bwel 3 9,825 22-04-2024, 03:21 PM
Last Post: JoeF
  Faac 415 can't reset from manual to operate mode Stephen Q 1 7,434 18-03-2024, 01:20 PM
Last Post: RXH
  Faac 455d Grantplant 1 8,011 13-11-2023, 11:58 AM
Last Post: Aiden Mitton

Forum Jump:


Users browsing this thread: