Hi
We sell the Q60S/R with our sliding gate automation (Kit Roller 8 & 15). From reading your post it sounds like the photocells are tripping, but only when the gate is opening. This is what is called the Opening Cycle or Phase. More than often the photocells are wired in the Closing Cycle, this is where the gates open then close but the photocell beam is broken and the gates stop and reverse. It sounds like the photocells are wired in the Opening Cycle.
To check - on the control board the terminals are numbered 1 to 20. If the photocells are wired in the opening cycle I would expect to see a cable going to the photocell receiver out of terminal 4 and a link present between terminals 3 & 9. If this is the case, we can configure the photocells to the closing cycle by moving the cable from terminal 4 to terminal 3 and place link between terminal 4 & 9.
If you require further assistance please email us: support@gatemotors.co.uk
Kind Regards
Gate Motors Technical Support
We sell the Q60S/R with our sliding gate automation (Kit Roller 8 & 15). From reading your post it sounds like the photocells are tripping, but only when the gate is opening. This is what is called the Opening Cycle or Phase. More than often the photocells are wired in the Closing Cycle, this is where the gates open then close but the photocell beam is broken and the gates stop and reverse. It sounds like the photocells are wired in the Opening Cycle.
To check - on the control board the terminals are numbered 1 to 20. If the photocells are wired in the opening cycle I would expect to see a cable going to the photocell receiver out of terminal 4 and a link present between terminals 3 & 9. If this is the case, we can configure the photocells to the closing cycle by moving the cable from terminal 4 to terminal 3 and place link between terminal 4 & 9.
If you require further assistance please email us: support@gatemotors.co.uk
Kind Regards
Gate Motors Technical Support