(03-05-2022, 10:08 AM)SamA Wrote: Hi Nat,
It sounds as though it could be something mechanical on the gate causing it to see an obstruction, when the fault occurs what does the ECSbus LED flash? When you manually release the gate and push it from open to closed does any friction occur?
Hi SamA,
Thank you for your response. Apologies for only just seeing it.
I did as you suggested and the gate manually opens and closes freely past the problem point.
I even gave it a firm push as it was closing automatically and it fought against me from the same point where it gradually slows down before coming to a stop. It's the same sequence it does once it approaches the fully closed position.
Regarding ECSbus flashing: when issuing open or close comand there's 4 long flashes. Once it reaches the fully closed or fully open point and stops there's 2 long flashes. When the gate stops at the problem location when closing there's no long flashes, the constant quick flashing just keeps going uninterupted.
Any ideas what this means?