hi
there is no programing option only trimmers regulation need it
trimmer TL2 set to minimum (working time second gatewing )
trimmer TRC set to minimum ( opening and closing time delay )
trimmer F motor force
trimmer TP pause time for automatic closing
make motor conection to 8/9/10 terminal M1
there is also dip-switch terminal from 1 to 10
two first one are important for right working
1/2 off/off manual operation
1/2 on/off semiautomatic
1/2 off/onn automatic (TP trimmer for closing time have to be set )
1/2 on/on automatic ( always closing option)
there is no programing option only trimmers regulation need it
trimmer TL2 set to minimum (working time second gatewing )
trimmer TRC set to minimum ( opening and closing time delay )
trimmer F motor force
trimmer TP pause time for automatic closing
make motor conection to 8/9/10 terminal M1
there is also dip-switch terminal from 1 to 10
two first one are important for right working
1/2 off/off manual operation
1/2 on/off semiautomatic
1/2 off/onn automatic (TP trimmer for closing time have to be set )
1/2 on/on automatic ( always closing option)
Best Regards
Tom
Automatic-TC