PROTECO Q60S/R FAULT AND INSTALL
#2
Hi

The Q60SR control board for swing gates showing "GO" error means that the control board is receiving a constant start signal caused by a closed circuit across terminals 1 & 8 (manual start command). This can be caused by incorrect wiring of push button switches, intercom connections and loop detectors. Anything that starts the gate other than the remote control key fobs will generate a "manual start command".

I would first remove all wiring from just terminal 1. This will remove the "GO" error and the gate may start. If it does, wait for the operation to complete, then you will see "- -" on the screen (stand by mode). Once this is seen, re-introduce one connection at a time back to terminal 1 until you see "GO" appear and stays there. As long as you know which piece of equipment is identified to terminal 1, you will be able to pin-point the unit causing the short.

If you require further info, please contact us as Gate Motors - support@gatemotors.co.uk

Kind Regards

Gate Motors technical Support
01202 717191