bft deimos ultra bt600 error f1 - pfloyd - 14-09-2024

Hi guys, I've beenĀ  using a BFT Deimos Ultra BT600 sliding gate opener for about 5 years now and I have never had any issues with it until a week ago when, after a rainy day, the device started malfunctioning. It opens the gate normally, but then it refuses to close it neither by remote nor through the respective button on the board. When I press any of the "close' buttons 'ERF1' appears on the display. The manual suggested checking the connections to the 'limit switch' which I did but to no avail. Next I did a hard reset, as described in the manual and the problem was solved. A week later though, after another rain, same problem appeared again. I'll reset it once again but I'm wondering what may be causing the malfunction to persist. Does any one have any idea what may be the reason for this particular error? Looks like it is rain/humidity related but why now? In the past five years or so it had rained and snowed hundreds of times but it had neverĀ  caused any problems. Any input will be highly appreciated.


RE: bft deimos ultra bt600 error f1 - Michael - 18-09-2024

Hi,

This is a photocell issue.


ER01 Photocells faulty test Exchange of photocell's contacts hasn't been detected or has taken place beyond the useful test time.
- Check the wiring of tested photocells
- Logics setting: photocells Test is active
- Check hardware failures on photocell's Rx or Tx
- Check presence of power supply on 24V output and/or starting of 24V Vsafe power supply
- Repairs: replace relays or components on 24V or 24V vsafe power supply circuit, components on inputs circuit

Regards
Mike


RE: bft deimos ultra bt600 error f1 - pfloyd - 18-09-2024

It is ERF1 and not ER01. Thanks for the suggestions anyway, but I have never installed photocells on this gate.
Rgds