Nice mc842h cable connection to gate lock - Andy-can - 05-07-2018

Hello 

Does the cable used to vonnect the gate conyrol unit need to be sheilded?   Total run from control unit to lock 15 meters.  Sorry to ask but have a unit usinh sheilded cable with outer sheild not grounded at any point. And looks like the original installer used what ever was available


RE: Nice mc842h cable connection to gate lock - Automatic-TC - 06-07-2018

hi

is that wire used for operating that gate (push button ? )
if the wire is buried together with power cable yes it have to be shielded.


RE: Nice mc842h cable connection to gate lock - Andy-can - 06-07-2018

Hi.

Cable is used to drive a 12 volt strike lock. And partialy run with the power cable. I will run sheilded if i csn find in town. In rural Spain so not easy for parts.


Thanks


RE: Nice mc842h cable connection to gate lock - Automatic-TC - 06-07-2018

shielded cable is not required in this case